We regularly install the electrical for Floating fountains. There are several instances when we are asked to trouble shoot existing installations so I want to have a btter understanding of these motors and motors ingeneral. This is the most current mystery:
4 - 460V 3ph 30hp motors. (2@750', 1@ 500', 1@200')
each is running at 49A under load.
Source voltage is 480V (490 Actual)
These motors will run for as much as a week and one or sometimes two will either trip the over loads in the control panel or the 60A breaker feeding the control panel. Including the shortest 200' run while the long runs are still fine.
There is #8 Cu run to each of the fountains from the lakes edge. #6 run from the source to the lakes edge.
Am I able to check for actual VD while under load? I only have access to the first 50' of the run to the motor. Is the Voltage consistent the entire length?
I do understand the #8 is maxed out when considering VD recomendations but why would the issue be so inconsistent? The cable and conductors are run under water and underground.
Looking for some insight on troubleshooting motors, how to check actual VD under load, and any recommendations for these type installations. I am sure you'll have questions and I will try to respond in a reasonable amount of time.
4 - 460V 3ph 30hp motors. (2@750', 1@ 500', 1@200')
each is running at 49A under load.
Source voltage is 480V (490 Actual)
These motors will run for as much as a week and one or sometimes two will either trip the over loads in the control panel or the 60A breaker feeding the control panel. Including the shortest 200' run while the long runs are still fine.
There is #8 Cu run to each of the fountains from the lakes edge. #6 run from the source to the lakes edge.
Am I able to check for actual VD while under load? I only have access to the first 50' of the run to the motor. Is the Voltage consistent the entire length?
I do understand the #8 is maxed out when considering VD recomendations but why would the issue be so inconsistent? The cable and conductors are run under water and underground.
Looking for some insight on troubleshooting motors, how to check actual VD under load, and any recommendations for these type installations. I am sure you'll have questions and I will try to respond in a reasonable amount of time.