Hello –
I never quite understood the whole 1 HP is equal to .746kW formula.
Especially if you compare it to the NEC motor tables.
Take for example a 10HP motor @ 208 3phase
The whole .746kW per HP suggests this motor a 7.46kW load.
The NEC table (which according to 430.6 is what I am to use to determine FLA to size OCP among other things) lists this motor at 32.2FLA So using a pf of .8 it works out that the motor is 9.3kW.
I have a project with many motors and the process engineer lists all the motors in the building as HP and as kW. When I checked the math they are using the .746/HP for each motor. I feel better converting every motor to kVA based on NEC chart to get actual power for all the motors and sizing the transformer feeding the building . This way the apparent power will be less based on the motors power factors.
Appreciate the thoughts anyone can offer on this subject.
I never quite understood the whole 1 HP is equal to .746kW formula.
Especially if you compare it to the NEC motor tables.
Take for example a 10HP motor @ 208 3phase
The whole .746kW per HP suggests this motor a 7.46kW load.
The NEC table (which according to 430.6 is what I am to use to determine FLA to size OCP among other things) lists this motor at 32.2FLA So using a pf of .8 it works out that the motor is 9.3kW.
I have a project with many motors and the process engineer lists all the motors in the building as HP and as kW. When I checked the math they are using the .746/HP for each motor. I feel better converting every motor to kVA based on NEC chart to get actual power for all the motors and sizing the transformer feeding the building . This way the apparent power will be less based on the motors power factors.
Appreciate the thoughts anyone can offer on this subject.