peterlevitt
New member
- Location
- New York City
When is it safe to use wire nuts for connecting incoming power to motor leads? At what amperage or conductor size, should un-insulated crimp on lugs & nut/bolts be used?
We have a customer who wired a 20 HP motor (230 volts, 46 FLA) to #6 or #4 lines with wire nuts. Our 60 amp AJT fuses blew immediately. We feel this was caused by the high resistance connections of the wire nuts & want them to be changed to lugs. We will also increase the fuses to 80 amps.
The electrican says the wire nuts comply with NEC. Help!
We have a customer who wired a 20 HP motor (230 volts, 46 FLA) to #6 or #4 lines with wire nuts. Our 60 amp AJT fuses blew immediately. We feel this was caused by the high resistance connections of the wire nuts & want them to be changed to lugs. We will also increase the fuses to 80 amps.
The electrican says the wire nuts comply with NEC. Help!