For 1/3 HP or less, per 210.21(B)(1) Exception 1.Should run with on a 20 amp circuit with a no problem.
First of all a 3/4 HP sump pump is not really a 3/4 HP motor, its marketing. Most 3/4 HP sump pumps I run across show around 10 amps on the label.If a 3/4 HP (13.8), 120V sump pump were to be connected to a duplex receptacle, how would this work if the circuit breaker would be 35 amps (13.8 x 2.5) yet the duplex receptacle would be just 20 amp?
A language change in the 2023 code to 210.21(B)(3) says otherwise.You can not protect a 15 amp duplex receptacle or 20 amp receptacle with larger than a 20 amp overcurrent device.
I don't think so.factory installed cord and plug is designed to plugged into a circuit base on the rating on the plug.
Those might be useful if you wanted to burn your house down for the insurance moneyI don't think so.
Unless it's listed as an assembly, which most are not.