The only instance that springs readily to mind that would require this is the installation of grounding receptacles on an ungrounded laundry circuit which would necessitate the GFCI. Also agreeing with Ron, the load should not be an issue.I agree with ron. Yes you could use a GFCI breaker, but why?
Originally posted by jmmyers:
Right in the directions to the GFCI receptacle it states they are not intended to be used on motor loads
I have never heard of such a restriction for any GFCI device.Originally posted by jmmyers:
Unfortunately for me I have never had a GFCI breaker and I don't know if they can be used on motor load circuits. Are they limited to non motor load circuits like the receptacles?
680.5 Ground-Fault Circuit Interrupters.
Ground-fault circuit interrupters (GFCIs) shall be self-contained units, circuit-breaker or receptacle types, or other listed types.
As you can see 680.22 requires GFCIs for pump motors, and most pool pumps are higher HP than a washer or dryer.680.22 Area Lighting, Receptacles, and Equipment.
(A) Receptacles.
(1) Circulation and Sanitation System, Location. Receptacles that provide power for water-pump motors or for other loads directly related to the circulation and sanitation system shall be located at least 3.0 m (10 ft) from the inside walls of the pool, or not less than 1.5 m (5 ft) from the inside walls of the pool if they meet all of the following conditions:
(1) Consist of single receptacles
(2) Employ a locking configuration
(3) Are of the grounding type
(4) Have GFCI protection
Curt i agree with you completley we have about 1,100 t poles out there thats how many skill saws,sawzalls chipping hammers on gfci circuits ??Originally posted by luke warmwater:
I still don't get it either.
Where in the Code does it say 'water source' must have GFCI protection? Where in 210.8 does it require the laundry circut to have GFCI protection?
Your AHJ is not interpreting the Code, he is making up his own Code which is where the problem is. Unless there is a written legal addendum, the GFCI is Not required.
Where in PA is this and which Inspection agency? Or is this a 'one man show' inspector for a small town? Or better yet, is this a town inspector inspecting electrical work?