430.22 tells you to size the Branch-Circuit conductors at 125% of the ampacity of the motor as determined by 430.6(A)(1) - which tells you to use the NEC tables. This is for a continuous duty application. For other than continuous duty, refer to 430.22(E). So the "standard" method of sizing motor circuits already takes "continuous duty" into consideration.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Just for information's sake, 125% and 80% are reciprocals of one another. In other words, a load of 80% of circuit ampacity, and a circuit ampacity of 125% of the load, are the same thing.
 