m sleem Top-notch Сasual Dating - Real-life Females Location Usa Occupation Health Aug 14, 2019 #1 Can i supply 3 core cable without neutral to a 3 phase Y motor load? this is a client request, I think no as Per 250.24(C), am i correct?
Can i supply 3 core cable without neutral to a 3 phase Y motor load? this is a client request, I think no as Per 250.24(C), am i correct?
electrofelon Senior Member Location Cherry Valley NY, Seattle, WA Aug 14, 2019 #2 If the load does not need a neutral than you don't need to run one. That section you cited is for service equipment.
If the load does not need a neutral than you don't need to run one. That section you cited is for service equipment.
ptonsparky Tom Location NE (9.06 miles @5.9 Degrees from Winged Horses) Occupation EC - retired Aug 14, 2019 #3 m sleem said: Can i supply 3 core cable without neutral to a 3 phase Y motor load? this is a client request, I think no as Per 250.24(C), am i correct? Click to expand... Motors do not require neutrals, they do require an Equipment Ground.
m sleem said: Can i supply 3 core cable without neutral to a 3 phase Y motor load? this is a client request, I think no as Per 250.24(C), am i correct? Click to expand... Motors do not require neutrals, they do require an Equipment Ground.