Re: motor meg.
To: buzzlectric,
buzz, I have a manual that the AVO company has sent to me. This company was the former Biddle Megger company.
I have one of their manuals, called " A Stitch in Time". It is a complete guide to Electrical Insulation Testing.
On page 45, they discuss the One-Megohm Rule, and what that means is this.
Example: A 2400 volt motor should have a minimum insulation resistance of 2.4 megohms.
You are not wrong when you condemn a motor at 500 megohms, you are just going on the safe side.
buzz, as I stated in my last post, I would allow that motor to run at that low reading, but I would prepare to have it taken out of service for a overhaul.
On the subject of 4 to 20 ohms difference between phases of a motor winding. I do feel that the 20 ohm reading is a little bit high, telling me that I may have problems with the windings and would be best to take the motor out of service for a cleaning, overhaul, and possibly a dip in the insulating varnish tank.