We are in an old building that had things that were done by others that were 'somewhat' questionable to say the least. lol There was a debate about the motor sizing of the branch circuit conductors calculatin from the small vfd they are thinking of bypassing, (its feed by 15amp fused disconnect that is fed by a 20amp breaker).
Voltage present is 208volts 3 phase.
I didn't have my code book at the time, but my 'handsome/ugly book' says a 3phase 208volt 5hp 16.7 FULL load current is what we should use plus 125%. So technically 16.7x125%= 20.875 is the calculation I get and Since they plan to bypass everything (which again I dont recommend, as the vfd had overload protections adjustable). . .
Others ae saying since its just a 14 amp nameplate on motor they can use #14 for the 208v even though they said sometmes the motor start up would blow the 15amp fuses. . I tried to explain Full load current (the nec chart) vs full load amps (nameplate amps) is different in sizing the branch circuit.
The overload protection are sized at the nameplate amps (ie. the 15amp fuses) or setting on the vfd possibly? can go up to about max 125% possibly 140%? (need my NEC to sure of the 140%) if trip setting is still too low. 115% of name plate is what appears to be set at 115%x 14=. 16.1 if we do 125%x 14=17.5 140%x14= 19.6 But if they bypass everyting which I dont recommend, I think they might can use the 20amp breake even though that is above the 140% , but I have always rounded down for overload protection, and round UP for groundfault/short circuit protection and it appears since everything else is bypassed the 20amp breaker will function as both the overload and ground/fault short circuit protection. Did I make a mistake on this calculation? can you technically use the 20amp breaker (no fuses) even though its 19.6amps max calculation? Also, I couln't remember what the 010A means beside the 'usuable at 208v 14. I assume the 14 was the running amps of the motor itself at 208v.
When I get a chance I can double check my NEC code book 2023
Here is the nameplate
Voltage present is 208volts 3 phase.
I didn't have my code book at the time, but my 'handsome/ugly book' says a 3phase 208volt 5hp 16.7 FULL load current is what we should use plus 125%. So technically 16.7x125%= 20.875 is the calculation I get and Since they plan to bypass everything (which again I dont recommend, as the vfd had overload protections adjustable). . .
Others ae saying since its just a 14 amp nameplate on motor they can use #14 for the 208v even though they said sometmes the motor start up would blow the 15amp fuses. . I tried to explain Full load current (the nec chart) vs full load amps (nameplate amps) is different in sizing the branch circuit.
The overload protection are sized at the nameplate amps (ie. the 15amp fuses) or setting on the vfd possibly? can go up to about max 125% possibly 140%? (need my NEC to sure of the 140%) if trip setting is still too low. 115% of name plate is what appears to be set at 115%x 14=. 16.1 if we do 125%x 14=17.5 140%x14= 19.6 But if they bypass everyting which I dont recommend, I think they might can use the 20amp breake even though that is above the 140% , but I have always rounded down for overload protection, and round UP for groundfault/short circuit protection and it appears since everything else is bypassed the 20amp breaker will function as both the overload and ground/fault short circuit protection. Did I make a mistake on this calculation? can you technically use the 20amp breaker (no fuses) even though its 19.6amps max calculation? Also, I couln't remember what the 010A means beside the 'usuable at 208v 14. I assume the 14 was the running amps of the motor itself at 208v.
When I get a chance I can double check my NEC code book 2023
Here is the nameplate