Is it true you don’t need neutral for 3 phase motors?
Is it true you don’t need neutral for 3 phase motors?
Is it true you don’t need neutral for 3 phase motors?
To be clear, by “large”, he means typically 2,000HP and up, medium voltage motors. Not something the average electrician will come across very often in their career and when they do, it will likely be in a detailed engineered project with clear drawings and specifications telling you exactly what to do. People only implement differential protection on very high value assets where high speed detection of winding faults can mean the difference between thousands of dollars in down time versus millions.There is one “exception”. With wye connected large motors with differential relay protection the wye is grounded. It is not a neutral but depending on how it is wired the ground may be insulated.