Ok everyone this may be an easy one, but I am an apprentice and I am still learning so go easy on me......
I have a motor with name plate info. as follows:
115 Volts Single phase
7.9 Amps
2/3 horsepower
60 Hz
no service factor listed
40 degrees temp.
My lead man wants me to try and figure out what we need to do to install this motor NEC compliant. It will be installed as a blower motor in a drop ceiling that will draw hot air out of a data center, duty will be continuous.
I looked for at the motor table 430.148 and found no 2/3 horsepower motor. If the motor is not listed how do I come up with good full-load current value to calculate my OCPD with? Can I use the 7.9 amps? Or just reaching, can I use the 1/3 horsepower rating and multiply by two?
Thanks Kevin