Customer called last night with the problem that the VFD was ON, but the motor was not turning. No faults apparent or showing up on VFD or the control HMI.
There are 2 contactors on the load side of the VFD to run either of two motors. Logic to the PLC and the Enable contact on the VFD require that the selected contactor must be pulled in 2? seconds before the VFD starts.
Would the VFD show a fault if no load was connected? IDR what the minimum HZ setting is,but there is one.
Everything works this morning of course. They discovered that before I headed out.