The OCPD for multiple motors is the next computed DOWN for the OCPD of the largest motor + the sum of the remaining motor FLCs. Does this apply only to motors on the same pull box / junction box / motor control center OR to motors on multiple random circuit breakers on a 42-pole panelboard as well?
For instance, lets say 3 small 1 HP motors are connected on circuits 3, 19, and 41 on a 150 A main circuit breaker 42-panelboard. Each of the individual branch circuit circuit breakers are sized at 250% motor FLC. But the main 150 A circuit breaker is going to be a lot larger than the allowed "next size down" rule.
Is the main circuit breaker excluded from this next size down rule? Is there a place in the code that calls this out?
For instance, lets say 3 small 1 HP motors are connected on circuits 3, 19, and 41 on a 150 A main circuit breaker 42-panelboard. Each of the individual branch circuit circuit breakers are sized at 250% motor FLC. But the main 150 A circuit breaker is going to be a lot larger than the allowed "next size down" rule.
Is the main circuit breaker excluded from this next size down rule? Is there a place in the code that calls this out?