Why will a large motor overamp if you run it without a load?
For instance we were testing a motor we just replaced the bearings on before we put the belts backon.
It is a 3 phase 60HP motor, 480V on a GE soft start. The soft start stopped the motor and the code displayed said it was due to high amps.
 

kwired

Electron manager
Location
NE Nebraska
It isn't single phasing is it?

Did it accelerate to speed?

A motor with no coupled load usually runs well below FLA. If your 60 HP motor is 480 volt with FLA of 77 you may only see 15-20 amps with nothing connected.

It may have some winding damage - hopefully not from disassembling to fix the bearings - seen that happen before - luckily not on a motor that big.
 

kwired

Electron manager
Location
NE Nebraska
Are you sure the SS parameters are set correctly?

I thought about that some - not as hard to mess those up to that extreme as it may be with a VFD so I didn't mention it. Could have a failing SS control. Try starting the unloaded motor across the line and see how it performs. Maybe meg the windings first - just to rule out ground faults - soft starter can dampen those enough that there is no violent current - across the line will just go boom.
 