I'm reasonably certain it's not a good thing to do, but not sure what will occur: The designed called for the six fuel pumps on a multiple generator installation to be 120 volt, and the system was wired and installed to match this design. The fuel pumps were only available as 208 volt single phase. The contractor is suggesting rather than changing out the branch circuit breakers, the contactors, and motor overloads (all rated 130 volt), just add a 3 kVA, 120 - 208 volt, single phase transformer after each of the six individual contactor/motor overloads. The motors are only a 400 watt load. Placing a transformer between the motor and the motor overloads seems like a really bad idea, and not sure how you'd size the overloads, or whether they would provide the protection intended. Any experience out there would be appreciated.