Re: Motor overload protection
The context under discussion is Motor and Branch-Circuit Overload Protection, further it is for Continuous-Duty Motors, More Than 1 Horsepower. The NEC permits four options to accomplish motor and branch-circuit overload protection for continuous-duty motors that are more than 1 Horsepower.
One of those methods [430.32(A)(1)] is for a ??separate overload device that is responsive to motor current.? ?Separate? may be reasonably interpreted as either ?apart from the motor? since the other three methods require specific components that are integral to the motor or, as I believe, ?apart from other overcurrent functions? since it is specific to overload rather than short-circuit or ground fault.
In either case, the VFD meets the intent.
Recognizing the context of the entire NEC ??is the practical safeguarding of persons and property from hazards arising from the use of electricity,? does anyone reasonably believe there is risk of overloading the motor or branch circuits in the application as originally described?
And while we are at it, shocking as it may seem, while there are many listed ASD/VFDs that provide overload protection, "listing" itself is not an NEC issue here. Nor is it a FedOSHA one since it?s not on the ?List of Test Standards Recognized.? It may be a state or local issue ? that?s something I have to deal with regularly.
[ June 03, 2004, 04:49 PM: Message edited by: rbalex ]