Boss -
Been out in the field a week - just got back
I want to be really clear that in no way do I ever advocate compromising safety nor any installation practice that in any way is not in complete accordance with the NEC and any other known regulation.
I reread my post looking specifically for any thing that could have possibly been construed as not being in line with this philosophy.
Originally posted by 69boss302:
Setting overloads up is not a cost effective method of extending production.
Not sure where your are going with this. If you are saying the overloads can not be set up to the max allowed by the NEC I guess I don't agree. As you recall from my first post, I had said I would not set the overloads above the NEC max.
I saw my comment about the motor failing on the fourth start after the third ol trip as "working per design". The context of that discussion would include the discussions with the production crew/managers that they can't do that sort of stuff to motors (intentionally run the machinery past design spec). They will burn up. So they were aware that if they chose to do that, the motor would likely burn up. With the trouble we had been having, there had been discussions concerning that the motor will not stand repeated restarts after ol trips. They get too hot. I had suggested two starts per hour was all the motors would stand and live. So when they had told me what had happened, my response was, "Well let's see, you overloaded it to where it tripped three times in an hour and on the fourth start it burned up. Sounds to me like everything worked per design." I was pointing out that intentionally overloading a piece of machinery will cause failures.
Originally posted by 69boss302:
Your increase in the Service Factor of the motor with correct verification of properly sized overloads and wiring would be acceptable.
Glad you agree.
Originally posted by 69boss302:
OSHA, NEC and others have recognized the fact that when a motor burns up there are many other factors to take into account. One being FIRES! Motor burning up = Heat and lots of it, smoke and usually lots of that. If there is any grease from the associated gear box more than just the motor can burn up. Personnel Safety, again the motors burn up and people are exposed to possible fire's and breathing that smoke.
I'm not sure where this came from. Your are absolutely correct. FIRES are bad. Certainly nothing I would recommend under any circumstances. I probably wouldn't even need an OSHA code to tell me that.

The only thing I could see in my post was the comment about "run to failure". If it was that, well that is an RCM term (reliability centered maintenance). When one does the RCM studies on a system, the group considers all of the known failure modes (some groups also consider unknown modes.

) Safety aspects are considered as well as production. Depending on the safety considerations and reliability requirements, any one of several levels may be applied. Some examples are: An automatic starting installed spare; remote monitoring and shutdown; periodic testing and overhaul to insure satisfactory operating condition; spare parts located on site; and maybe even, run it till it fails and then put in a new one. Just in case you might be thinking these RCM studies are management tools to save money, could be, but all I been involved with were run by the techs. Have to be, they are the ones that really know the failure modes. The example I gave on "run to failure" was a small gear pump that ate up the gears. miserable little bear to change, but cheap. In that context, I not seeing an issue with FIRES. If it was something else, let me know, I'll provide the context or an immediate retraction.
Originally posted by 69boss302:
coulter: Today's engineering practices do with as minimum as they can get away with ...
Couldn't tell you about that. Most of the stuff I deal with has a spec, and the engineers/designers are paid to meet the spec, regulations, and codes in a cost effective manner. I guess I don't see that as trying to "get away" with anything.
Originally posted by 69boss302:
coulter: I'm sorry but with all the regulations out now and OSHA investigations it is not cost effective by any means to compromise safety for production.
No need to be sorry. I absolutely agree with you.
Originally posted by 69boss302:
Is it better to keep a machine running and produce 100 parts a day and get 500 at the end of the week. Or push it and get 200 parts one day, 50 the next...
That I don't know. And with out a cost analysis, how would you know? I likely would tend to agree, but that is different than knowing. Please remember, I am not advocating any safety related failures.
Originally posted by 69boss302:
Any time the motor burns up there should also be a check for why it burned up, not just OK change that motor again. Something is wrong, if a motor continually goes bad, it needs to be fixed.
Yes, generally that would be true. The case I stated above, I think the failure mode was well understood and we did change to one more suited to the use. I think that meet your criteria.
But then again, not always. Several years ago I had pair of 500hp, 3600rpm motors that would take out the bearings twice a year. I tell my boss the motor is under designed, it really should have had sleeve bearings instead of ball bearings. His response is, "Is it going to fly apart to where there is a safety issue." No, when the bearings start to go we see it on the vibration monitor, and take it off line." "Okay what does it cost to fix each time." "Six man-days and $1000 in bearings - say $4000." "So, you want to spend maybe $100,000 to mitigate $8000 in maintenance costs per year." What I did do, was spend about $20000 to balance the pump shaft and impellers and the motor shafts. Got the failures down to about one a year.
My point is that, yes, an analysis of failure modes is needed to insure safety and regulatory considerations are satisfied. Then a cost analysis is required to select a maintenance strategy. Just cause a motor burns up does not mean there is a design flaw that has to be fixed. There may be a design flaw :roll:
carl