Motor Overload Protection
Wire_nutz
Some times I see other electrical devices being feed off the motor/overload terminals of a motor starter. NEC article 430 only addresses overload usage with motors.
I have not come across any manufacture specifications that says it is permissible to size overloads with other electrical devices or controls. It has always been my understanding overload protection on a starter is for individual motor protection.
Are some doing this because the informational materials don?t actually say nothing else can be connected to the overloads with the motor? Also what is UL and OSHA impact on this?
overload taps
overload taps
In my old water utility job we would only tap above the overload to supply power to a relay or other small current device. This was only done if that device( by means of other detection) would stop during a motor overload. IE: chemical pumps tied into a well motor starter. It was a rule passed down from the board of health. I don't know if our situtation originated from NEC or OSHA.
Poor practice?
If you add non-motor related devices below the overload then 430 part III doesn't let you increase the size of the overload for them. 430 part III calculations limit the overload size to that required by the motor circuits.
Moderators please feel free to offer your input.
I am not getting much help here. Moderators please feel free to offer your input.
The NEC doesn?t say no other loads other than a motor may be connected to the motor terminals of a starter with a motor. The NEC does not say other devices shall not be connected on the ?T? terminals of a motor starter with a motor.
Motor starter manufacture starter specifications only mention motors connected to a motor starter with overloads.
Since the NEC does not say shall not, and the manufacture literature does not say you can not have other devices on the motor terminals with overload protection. Does this make it OK? Apparently people are doing it?
I am not aware of anything in the NEC that specifically prohibits connecting other loads to the load side of a motor starter after the motor overloads.
The biggest problem will be that the motor overloads must be sized at no more than 115% or 125% of the motors nameplate rating. This would make any load added after the motor overloads to either be very small or cause the motor overloads to trip. (Check out Part III of Article 430 for motor overload protection)
Chris
Everything depends on the overcurrent device protecting the motor starter, the overloads have nothing to do with it. The protective device must meet and be sized under the requirements of Article 240.
Table 240.4(G) grants an exception for motor circuits, not for motor starter overload relays. If the conductors do not feed motors article 430 is not applicable per 430.1.
Design Intension
Design Intension
Does the NEC require overload protection for motors? The specific size of the overload to be used is based on the current draw of the motor. By adding another electrical device on the same terminals as the motor would interfere with the sizing of the overload.
Combination motor starters are intended for a motor load and controls. The manufactures of the starters provide auxiliary contacts and control relays for the use of other electrical devices and are not connected to the motor over load terminals.
Normally most electricians use and wire a motor starter as intended by the manufacture. Is there any documentation by UL or OSHA or some other standard that a piece of electrical equipment must be used as it attended or designed for?
Your making a big deal over nothing. As long as the overload is sized according to the nec who cares. It then becomes a design issue which the nec doesnt cover most of the time. If these people want to take a chance on nuisance overload tripping then let them.
To answer your question, I to not know of anything that would say you could not do this.
Yes, check out Part III of Article 430
Correct
The NEC would require that the overload for the motor be sized off the motor nameplate FLC rating and you would not be permitted to increase the overload size for additional loads.
110.3(B) requires us to follow the installation instructions for a listed piece of equipment.
Chris
Normally? I am not sure you can speak for what most electricians do.
I agree but will be very surprised if there is anything in the listing that prohibits other loads.
I agree, I have never seen installation instructions from a combo starter that prohibited adding another load after the motor overloads.
Chris
Many Starters & Electricians
I started my career as an electrician in the field and I was exposed to motor starters at many locations and customers. Practically all of the motors starters did not have any other loads connected to them.
During my State Indentured Electrical Apprenticeship motor studies it was never mentioned to add other loads to a motor starter on the T terminals of the starter. All other loads to be served are too be connected ahead of the overload protection. The NEC Hand Book gives illustrations and examples of overloads and motors, not any other types of loads. Motor starter Manufactures literature, specifications and diagrams only show motors connected to motor starters with overload protection. With this information it sure looks like this is what a starter was designed for and how it intended to be used.
I was formally employed by a Very Large manufacturing facility as a maintenance electrician for many years with many other other electricians. The assembly lines had thousands of motor starters and I never came across one with other loads connected to the T terminals with a motor.
With all the motor starters out and about, I sure hope they are not being wired by people without an electrical background.