E elect36 Member Aug 9, 2005 #1 where can i find out about sizing up overload's on a starter for a 1 h.p. 1.7 amp motor.
L luke warmwater Senior Member Aug 9, 2005 #2 Re: motor overloads The paperwork that comes with the motor starter for one, or manufacturers web site is a great place.
Re: motor overloads The paperwork that comes with the motor starter for one, or manufacturers web site is a great place.
D danilo Member Aug 9, 2005 #3 Re: motor overloads you may size up your overload by multiplying the full-load current by 1.15. However,recommended setting by motor's manufacturer should prevail
Re: motor overloads you may size up your overload by multiplying the full-load current by 1.15. However,recommended setting by motor's manufacturer should prevail
L luke warmwater Senior Member Aug 9, 2005 #4 Re: motor overloads If you want the NEC reference, it's 430.32
L luke warmwater Senior Member Aug 9, 2005 #5 Re: motor overloads 1 h.p. and 1.7amps. Must be a 575v motor? NEver seen one of those. Got a spec?