I got this PM from a new member named mdb443.
I'd like your opinion. Would it be code compliant to use a MPCB (motor protector circuit breaker) to protect a motor, but also to tap off load side of MPCB to feed a .5kva control transformer BCP (branch circuit protector)?
The MPCB is cULus Listed as a Circuit Breakers and the BCP is UL489 listed. The tap to primary of control transformer is less than 3ft and does not exit the enclosure, but control transformer secondary could control motor contactor coil in the enclosure and a couple solenoid valves outside the enclosure. Is this code compliant?
Instead should I use a MCCB as feeder to motor contactor (with OLR on load side) and control transformer BCP?