motor protection
rjdad82
I have a new commercial facility that i am building and have a dishwashing room on the interior of the building. There are 2 washing motors one is 125 amp and the other is 60 amp, i have two disconnects that i am mounting within sight of the motors on an adjacent wall and they are weatherproof. I have been reading the code and am using a dual-element time delay fuse and will rate the fuse at 175% of the amperage. I have read further in section IX from 430.101 to 430.113 and have yet to find a part that specifies that i have to use a fused disconnect, is this just an option? The motor is thermally protected.
Re: motor protection
The thermal protection on the motor is "overload protection". The motor (and its branch circuit or feeder conductors) still require "ground-fault" and "short circuit" protection. Either a fuse OR a circuit breaker can normally provide this protection. But, if a device is marked "Maximum Fuse Size", fuses are required.
STeve