Motor Question

Kaito

Member
Location
Seattle
Occupation
Electrician
Studying to take my Admin and am confused on why they didn’t take into consideration of the service factor.

There are three motors; one 5hp, 230v, single-phase motor with a service factor of 1.20; and two 11/2hp, 120v, three-phase motors. Using an inverse time breaker, the 3-wire feeder conductor protective device after balancing all three motors will be ____.
(a) 60A
(b) 70A
(c) 80A
(d) 90A

The answer is D
 
only thing service factor typically does is make you use different motor overload setting if it is only 1.0 vs 1.15 or 1.25.

SCGFprotection is not impacted by service factor.
 
For SCGF protection you use the Tables.40.52 and 430.248 do not address service factor the way 430 Part III (overload) does,
 