LMartin57
Member
- Location
- Valrico, Florida USA
what part of the code should I refer to when using instant trip breakers on motor application.
see 439.52 table
You type as bad as I do.
Pay particular attention to 430.52(C)(3).
(3) Instantaneous Trip Circuit Breaker. An instantaneous trip circuit breaker shall be used only if adjustable and if part of a listed combination motor controller having coordinated motor overload and short-circuit and ground-fault protection in each conductor, and the setting is adjusted to no more than the value specified in Table 430.52.
I agree with Gus, this is most important An instantaneous trip circuit breaker shall be used only if adjustable and if part of a listed combination motor controller.
You cannot install one in a panel.
I agree with Gus, this is most important An instantaneous trip circuit breaker shall be used only if adjustable and if part of a listed combination motor controller.
You cannot install one in a panel.
I do not see it as a myth I see as applying the code section as written
where in the code does it require the thing to be in an enclosure to be a listed assembly?
and if part of a listed combination motor controller
To me that does.
A panelboard is not typically a combination motor controller.
so all the UL listed assemblies that include an MCP that are not sold in an enclosure are not code legal? is that your contention?
and who said anything about a panelboard?
You cannot install one in a panel.
sure you can, as long as you install it as part of a listed combination. what you can't do is make up your own combinations of parts.
You cannot install one in a panel.
Time to split hairs.
Yes they can be installed in panels (Square D ones are available in I-Line construction), however they cannot be installed as branch circuit protective devices (e.g. when the load conductors leave the panel). So, if the panel also contained the motor starter (e.g. think custom enclosure), the installation might be compliant.
How are you related to the electrical industry?
I work regularly as an electrician in construction
Before anyone gets upset I am joking, I have much respect for engineers and what they do. It is just that we often speak different languages.
Recently I had problem with a instantaneous trip breaker in a new installation. The panel come with a 35 amp breaker which was to feed a VFD controlling a blower with a 10 hp motor, 208 volts 3 phase, wire size #8. The problem was if you put the VFD in manual the breaker would trip upon start up. According to NEC 430.52 how would you calculate the correct breaker size.