Motor Rated Switch vs Non-Fused Disconnect Switch

Location
Texas
Occupation
Fire Alarm Tech
Wanting to pick some of yalls brains on the two different types of switches. Most of my WAHP switches are shown to be connected to a 30A non-fused disconnect switch (safety switch) either to 480V 3P or 208V 1P. Protection would be provided at the circuit breaker since these are non-fused disconnects. Any reason to not use a motor rated switch in place of the safety switches for all 30A units?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
WAHP? Some sort of Heat Pump?

Motor rated disconnects, usually listed under UL508C as a form of "manual motor controller", can only be used for motor loads, whereas a UL98 listed "safety switch" can be used anywhere. So if it is a heat pump and has a motor, then yes, you could use the UL508 listed motor switch.
 