Correct me if I'm wrong but isn't E over I/R the correct table for motor readings? I had 2 motors recently, both new, 208/240, 2.1 amp. Ohm reading should be somewhere about 99 to 114. One was 40 something, the other 60 something. Same labels on both. What am I missing here?
Also, is a motor listed for 208/240 OK on 277? Some of my coworkers say yes, some no. These are hand dryer motors and we have some dryers on 277. I haven't had a chance to replace one of them and pull the motor to verify.
Thanks for any feedback.
Also, is a motor listed for 208/240 OK on 277? Some of my coworkers say yes, some no. These are hand dryer motors and we have some dryers on 277. I haven't had a chance to replace one of them and pull the motor to verify.
Thanks for any feedback.