AC unit shows manual starting switch and the symbol is shown on the E drawings symbol list as shown below. When referencing the mechanical schedules for AC units( and this particular one) it says " provide unit mounted local disconnect switch". Is that the same device as the manual starting switch and thus a conflict or a different device entirely? Thanks.

1726752801897.png
1726752820427.png
1726752844675.png
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Hopefully your plans show if T2 is located at the unit.
If T2 js located out of sight of the unit, a disconnect would need to be at the unit.
 