A motor has stator rtd's and and the motor says they should alarm at 135deg C and trip at 140deg C Motor is rated for 85deg c temp rise at 40deg ambient.
If motor is operating in ambient and operating at full load should the rtd's hit the alarm or trip setpoints under normal conditions?
Seeing a 85deg rise I would think under normal conditions the motor would operate at full load at 125deg C based on rated rise, and there would be a 10deg allowance for hot spots. Is this correct.
Running at full load under ambient conditions what are the max values on rtd's that I should see? 125deg C?