Can we use adjustable MCP for overload and short circuit motor protection?
I will rephrase the question,
Is it mandatory as per NEC to use separate o.l for motor protection or the adjustable MCP Can do the job for short circuit and overload protection?
An MCP is an instantaneous (magnetic) only device. It cannot provide overload protection as it does not have a long time trip function.
I will rephrase the question,
Is it mandatory as per NEC to use separate o.l for motor protection or the adjustable MCP Can do the job for short circuit and overload protection?
So that, any breaker provide LSI trip (long, short, instantaneous) would qualify and meet NEC requirements & no need of having separate overload protection.An MCP is an instantaneous (magnetic) only device. It cannot provide overload protection as it does not have a long time trip function.
I have never seen any substantial motor that could be run without overload protection. Overload protection is very different that short circuit and ground fault protection which, I believe, is what you get from an overcurrent protective device.
No. A thermal magnetic breaker sized large enough to permit the motor to start will be too large to provide overload protection. Also assuming the motor is over one horsepower, a breaker is not one the overload devices that are permitted by 430.32(A).So that, any breaker provide LSI trip (long, short, instantaneous) would qualify and meet NEC requirements & no need of having separate overload protection.