motor short circuit /grd fault

Status
Not open for further replies.

papa

Member
Location
South Carolina
A while back I did a job as directed by employer that I have questioned whether it was code complyent.

3 , #6 thhn c. ran from a 60 amp 480 volt breaker , with # 10 grd.to a 60 amp N/F disconnect , tapped in a trough to # 10 ran to 4 manual motor starters ,then on to 4, 3 hp 3 phase motors. See anything wrong?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
430.52 would require a 15 amp breaker or a 10 amp fuse as the maximum GF-SC protection.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
430.52 would require a 15 amp breaker or a 10 amp fuse as the maximum GF-SC protection.

Yep. If they are NEMA style thermal only manual motor starters, then you must "group fuse" them as augie47 says.

Most of the IEC style MMS units are already UL listed for group fuse installations all by themselves because they have the short circuit instantaneous trips built-in. That may be where they got the idea, but it sounds like they extended the concept to something not suitable for use like this.
 

mull982

Senior Member
Yep. If they are NEMA style thermal only manual motor starters, then you must "group fuse" them as augie47 says.

Are you saying that one fuse can provide the short circuit protection for all 4 motors as opposed to having a fuse or short circuit protection for each of the 4 motors individually? Is this mentioned in 430.52?
 