malachi constant
Senior Member
- Location
- Minneapolis
Hi all,
We have a new lift station pump with 39.2 FLA / 49 MCA. We specified this being fed from a 60A manual transfer switch, which in turn is fed from a 60A circuit breaker on the normal side, and on the "emergency" side a 60A twist lock receptacle for portable generator to plug into.
We are getting close to installation and the motor manufacturer states they require a 100A breaker. This is easy enough to accommodate (there is an existing breaker that size in the panel). Normally I would be comfortable specifying #6 wire (60A) for this size motor even with the larger OCPD, because code allows it, overload protection is built into the motor, etc.
1. But does the presence of the transfer switch change things? I'm thinking that needs to increase to 100A to match the breaker size.
2. Once you've done that do you need to also upsize the wire between breaker and motor (through the transfer switch) to #3s/100A?
3. At that point you should probably be consistent and upsize the wiring and twist lock receptacle on the "emergency" side of the transfer switch to 100A. (Though I do not believe this is required by code.)
Would appreciate some code clarification on this, especially on items #1 and #2. I'm not sure if I explained this very well. Let me know if you need anything clarified. Thanks!
Thanks!
We have a new lift station pump with 39.2 FLA / 49 MCA. We specified this being fed from a 60A manual transfer switch, which in turn is fed from a 60A circuit breaker on the normal side, and on the "emergency" side a 60A twist lock receptacle for portable generator to plug into.
We are getting close to installation and the motor manufacturer states they require a 100A breaker. This is easy enough to accommodate (there is an existing breaker that size in the panel). Normally I would be comfortable specifying #6 wire (60A) for this size motor even with the larger OCPD, because code allows it, overload protection is built into the motor, etc.
1. But does the presence of the transfer switch change things? I'm thinking that needs to increase to 100A to match the breaker size.
2. Once you've done that do you need to also upsize the wire between breaker and motor (through the transfer switch) to #3s/100A?
3. At that point you should probably be consistent and upsize the wiring and twist lock receptacle on the "emergency" side of the transfer switch to 100A. (Though I do not believe this is required by code.)
Would appreciate some code clarification on this, especially on items #1 and #2. I'm not sure if I explained this very well. Let me know if you need anything clarified. Thanks!
Thanks!