I am running a 50 hp motor 460v 1800 rpm it keeps tripping a 80 amp breaker before the starter about every 4 hrs is the motor possibly bad?
ive done all of the above
an 80 amp breaker for a 50 hp 460 volt is WAY SMALL.
Unless it is an IT-only (Instantaneous Trip) breaker (a.k.a. MCP) that has no thermal trips, which is what is mostly used in combination starters...I'd agree that the 80A breaker is too small. Replace it with a 150A c/b and see if the problem persists.
I'd guess that your loading an 80% rated 80A (64A) circuit breaker near or above the 80% level with a continuous load (50HP-460V = 65A FLA by T430.250.) So after several hours of continuous load, it trips.
ive done all of the above
Unless it is an IT-only (Instantaneous Trip) breaker (a.k.a. MCP) that has no thermal trips, which is what is mostly used in combination starters...
dshelley,
You need to look more closely at that "80A breaker" to determine what kind it is, post a part number if you aren't sure and we'll help. If it is an IT-only breaker, then that's a completely different issue in terms of what could make it trip. If it's a Thermal-Mag (TM) breaker, then the above issue is probably the cause.
You're right, IT breakers in that range either come in 50, 70, or 100A depending on mfr. Didn't think of that.It is likely not an MCP as their continuous ratings, which are printed on the handle/toggle is either 70A or 100A. A 50HP starter would require a 100A continuous rated MCP with a recommended adjustable trip rating of
300-1000A.
So an 80A T&M CB would definetly be under-rated.
Still comes down to the OP providing more info and he seems to have checked out.