brian john
Senior Member
- Location
- Kilmarnock, Va
- Occupation
- Retired after 52 years in the trade.
Having a discussion regarding Time Delays for Phase Loss Relays (single-phase, UV, OV, or Reverse Phase) in regards to Motor Starting. Assume a facility has a single-phase condition and an attempt is made to start a 3-phase motor, what would be the maximum delay you would want for the Phase Relay? Some are saying instantaneous, I think some time delay is possible as the motor can handle inrush currents on start-up and single-phase currents would be somewhat similar to inrush but only for a much longer duration if the motor is not removed from service. Another point was brought up that the Thermal Overloads should protect the motor and it was cited that Bussman literature that states their Low-Peak or Fusetron fuses if properly sized will protect motors from Single-phase conditions
The issue arose around the practice of installing Phase Loss Relays on the Main (Fused Pressure Switch or CB manually operated to close) for a facility with no downstream motor phase protection, other than fuses and overloads. I believe phase loss for motors (UV, OV Single Phase) protection should be installed in MCC, a single Phase loss with controls too prevent startup and stop any running motors or Phase protection for individual motors in the starters. The advantage is an EMS system can restart the motors once the single-phase condition is resolved. With protection at the main fused BPS or CB would require an electrician to come to the facility, determine the cause of why the Main opened and close the Main. With overloads and fuses, it has been my experience that they are more often than not improperly sized, using Name Plate in lieu of actual full load running current, which would negate the protection.
The issue arose around the practice of installing Phase Loss Relays on the Main (Fused Pressure Switch or CB manually operated to close) for a facility with no downstream motor phase protection, other than fuses and overloads. I believe phase loss for motors (UV, OV Single Phase) protection should be installed in MCC, a single Phase loss with controls too prevent startup and stop any running motors or Phase protection for individual motors in the starters. The advantage is an EMS system can restart the motors once the single-phase condition is resolved. With protection at the main fused BPS or CB would require an electrician to come to the facility, determine the cause of why the Main opened and close the Main. With overloads and fuses, it has been my experience that they are more often than not improperly sized, using Name Plate in lieu of actual full load running current, which would negate the protection.