Walters
Member
- Location
- Berkley County West Virginia
Car lift company installed a new lift and tapped off a circuit sharing other equipment. Lift shuts off at start up because everything is undersized. They installed 12/2 romex, exposed from the motor to a standard none fused disconnect that was sharing other equipment (Tire Machine). Circuit is being feed with #12 copper off a standard GE 20 amp breaker almost 100 feet away. I attached the motor pictures, it does not tell me FLA only max working load amps 24.5 amps.
Off this information I believe I should size the conductors at 125% (30.325 amps) #10 off the 75 Deg.
I believe I should size the breaker at 250% which would be 61.25 amps next fuse size at 70 amps. At start up it showed 65 amps and flashed 80 amps on the wire doing a amp probe.
With the disconnect sharing the other equipment I plan to separate this and let the tire machine have its own 20 amp 2 pole breaker, no disconnect because it has a twist lock plug.
I would like to re-use the standard non fuse disconnect or would I need to install a fused discconet with dual element fuse at 125% (35 amp fuse)
Thanks for reading and your help
Off this information I believe I should size the conductors at 125% (30.325 amps) #10 off the 75 Deg.
I believe I should size the breaker at 250% which would be 61.25 amps next fuse size at 70 amps. At start up it showed 65 amps and flashed 80 amps on the wire doing a amp probe.
With the disconnect sharing the other equipment I plan to separate this and let the tire machine have its own 20 amp 2 pole breaker, no disconnect because it has a twist lock plug.
I would like to re-use the standard non fuse disconnect or would I need to install a fused discconet with dual element fuse at 125% (35 amp fuse)