journeyman0217
Senior Member
- Location
- Tennessee
- Occupation
- Electrician

I am trying to size the conductors supplying this motor. it is for an air compressor which would turn on automatically as pressure gets to a certain psi. it is for a small shop so the compressor would only kick on maybe once or twice a day. I would consider this motor a non-continuous duty motor and would refer to table 430.22(e). (i'm using a 2008 code book right now because phila is still using 08' code) am I correct in referring to this table? and if so i'm confused on what classification of service I would use...(varying duty?). and the second part of this question is, this motor is rated 5hp @230v. 430.6 says to size conductors according to table 430.248. my supply voltage is 208v (which will lead to another question, 230v rated motor on 208v supply) if trying to find the FLC of the motor would I use the 208v column of the chart if the motor is rated at 230v? hope the picture I posted is readable...if not the nameplate states: 5hp single phase RPM 1740, SF 1.15 , 230v 25amps