All,
Been reading this forum for years, lots of info and expertise here.
Motor OCPD, overload, and circuit sizing is definitely a confusing topic. I am going to be installing a new air compressor shortly, and I want to make sure I have everything correct and want your expertise to make sure I understand everything.
First of all, it is a continuous duty rated 3HP single phase 230V motor with a nameplate FLA of 15A. I have also acquired a 5HP magnetic starter/controller (I realize it is bigger than I need, but it was a good price).
1) The FLC is to be computed via 430.248, which is 17A
2) Since it is continuous duty, the conductors need to be sized at 125% of FLC, which is 21.25A
3) If I were to run NMB cable, I would need to run #10. However, if I pipe it and use THHN, or I use MC, I could get away with #12, since the small conductor rule normally limiting #12 to 20A does not apply to motors, and I can use the 75 degree column for 25A? Do I have this correct?
4) I have a 30A disconnect switch rated for 3.0HP, but since I am only using it as a disconnect, its horsepower rating really doesn't matter anyways and it is only the 30A rating that counts. The disconnect needs to be sized 1.15 times the continuous FLC of 21.25A above, which works out to 24A, so I am good there? Correct?
5) I sized the overload heater based on the FLA of the motor.
6) The OCPD can be up to 250% of FLC...or up to 42A, correct? So, a 45A breaker due to next size up rule?
7) The control wires, which are tap off of the supply side wires coming into the magnetic starter/controller and head to the pressure switch several feet away need to be protected by a supplemental OCPD or must be at least 14AWG per 430.72(b) column C.
Anything else I am missing or not thinking of to make for a nice safe install?
I realize I am making a mountain out of a mole hill here, but I just want to make sure I understand it all.
Thanks to everyone for any feedback.
Been reading this forum for years, lots of info and expertise here.
Motor OCPD, overload, and circuit sizing is definitely a confusing topic. I am going to be installing a new air compressor shortly, and I want to make sure I have everything correct and want your expertise to make sure I understand everything.
First of all, it is a continuous duty rated 3HP single phase 230V motor with a nameplate FLA of 15A. I have also acquired a 5HP magnetic starter/controller (I realize it is bigger than I need, but it was a good price).
1) The FLC is to be computed via 430.248, which is 17A
2) Since it is continuous duty, the conductors need to be sized at 125% of FLC, which is 21.25A
3) If I were to run NMB cable, I would need to run #10. However, if I pipe it and use THHN, or I use MC, I could get away with #12, since the small conductor rule normally limiting #12 to 20A does not apply to motors, and I can use the 75 degree column for 25A? Do I have this correct?
4) I have a 30A disconnect switch rated for 3.0HP, but since I am only using it as a disconnect, its horsepower rating really doesn't matter anyways and it is only the 30A rating that counts. The disconnect needs to be sized 1.15 times the continuous FLC of 21.25A above, which works out to 24A, so I am good there? Correct?
5) I sized the overload heater based on the FLA of the motor.
6) The OCPD can be up to 250% of FLC...or up to 42A, correct? So, a 45A breaker due to next size up rule?
7) The control wires, which are tap off of the supply side wires coming into the magnetic starter/controller and head to the pressure switch several feet away need to be protected by a supplemental OCPD or must be at least 14AWG per 430.72(b) column C.
Anything else I am missing or not thinking of to make for a nice safe install?
I realize I am making a mountain out of a mole hill here, but I just want to make sure I understand it all.
Thanks to everyone for any feedback.