Motor start on a VFD

Status
Not open for further replies.

wbdvt

Senior Member
Location
Rutland, VT, USA
Occupation
Electrical Engineer, PE
Hello, I have reviewed information on VFD's and understand how they function with a load. I either missed it or can't find it but how does a VFD affect motor start? Is the starting curve the same for a motor on a VFD as it is for a standard across the line starter?

Thanks in advance.
 
Hello, I have reviewed information on VFD's and understand how they function with a load. I either missed it or can't find it but how does a VFD affect motor start? Is the starting curve the same for a motor on a VFD as it is for a standard across the line starter?

Thanks in advance.
No, not at all the same.

You get to set the parameters of how it starts/stops.
Have you played with one yet?
 
No, I have not played with one. This is on a York Chiller YK and the info I can find indicates that upon startup the chiller will always go to full speed.
 
No, I have not played with one. This is on a York Chiller YK and the info I can find indicates that upon startup the chiller will always go to full speed.
It could operate at above greater than full speed.
 
York would not bother with the extreme cost of adding a VFD and not use it to modulate speed. On a Chiller, it might BEGIN at full speed, but will change the speed based on the requirements for coolant flow. If it never changes speed, it was a total waste of money and energy, a Soft Starter would have been a better choice.

When VFD accelerates a motor from standstill, the motor starting current is completely controlled by the VFD at all times. In addition, the motor power factor is also being controlled, so the current going to the motor is almost all going toward creating torque, where as the high starting current from starting a motor Across-the-Line is mostly reactive at first, meaning NOT yet producing torque, until the motor gets to around 80% speed. So using the VFD, you can accelerate the motor without ever exceeding the motor nameplate FLA, so long as acceleration time is not a concern. In a chiller it usually is, so it might go higher to maybe 150% of FLA for a brief time, but never the 600% you see Across-the-Line.
 