I have a concern with voltage drop.
We have a 750' of number 8's with 10HP, 3Ph, 480Vac, Squirrel Cage Motor with an FLA of 14
2.81% Voltage Drop at full load FLA of 14Amps
17.31% Voltage drop at locked rotor FLA of 83Amps
I tried discussing with Baldor (the motor manufacture) if the pump will be able to get over the momentary locked rotor voltage drop.
At locked rotor the FLA puts the voltage at 397.
Will this be sufficient to get this pump going? :-?
Any help will be greatly appreciated.