I wouldn't and I don't see the need for it with a VFD but I don't know if your code requires it.If a VFD is used with a motor, is a motor starter required to be used in addition to provide the motor overload protection? Or is overload protection typically provided in the VFD as well?
No dispute with that.The OP mentioned "a motor".One of the more typical exceptions to this is if a single VFD is driving multiple motors, then you would need individual overload protection for each motor. But you should connect it so it gives a fault input, loss of enable input, or a stop command to the drive and not just take that one motor directly off line when it trips on overload.
One of the more typical exceptions to this is if a single VFD is driving multiple motors, then you would need individual overload protection for each motor. But you should connect it so it gives a fault input, loss of enable input, or a stop command to the drive and not just take that one motor directly off line when it trips on overload.
If a VFD is used with a motor, is a motor starter required to be used in addition to provide the motor overload protection? Or is overload protection typically provided in the VFD as well?