A customer wants to use a spare MCC bucket to control an on-off resistive process heater at their plant.
I've said it would only be possible if they replaced the MCP breaker in the bucket with a new thermal-mag breaker, as MCPs are only allowed for motor circuits. However in looking at article 430, I only see that MCP needs to be part of a listed motor controller - but not that the motor controller has to be feeding a motor.
Is there somewhere in the NEC that would allow a standard starter with MCP and OL relay to feed a non-motor load that I am missing? (customer is not in agreement).
I've said it would only be possible if they replaced the MCP breaker in the bucket with a new thermal-mag breaker, as MCPs are only allowed for motor circuits. However in looking at article 430, I only see that MCP needs to be part of a listed motor controller - but not that the motor controller has to be feeding a motor.
Is there somewhere in the NEC that would allow a standard starter with MCP and OL relay to feed a non-motor load that I am missing? (customer is not in agreement).