FNCnca said:
I guess my last post was more directed at the quote. I did not think that any disconnects were listed as starters.
I do know that in my company, you better not use a disconnect as a load break device except in the case of an emergency.
To answer your earlier question (and this one), No, a disconnect cannot be listed as a "starter" because of the definition of a "starter", but Yes there are disconnect switches that are rated for motor starting duty. Or rather, most disconnects are so rated, although the rating may be for a motor load far smaller than the amp rating of the disconnect. In most catalogs for disconnect switches they will provide you with an amp rating, and then separately, a motor load rating in HP or kW. There are a few really cheap disconnects that do not have a motor rating, but they are actually somewhat rare because it just means the manufacturer was too cheap to even try!
That said, just because you CAN do it, doesn't mean it is OK to do it. You still need to have ALL of the necessary protections in your motor circuit, including running overload protection. That can be very difficult to attain on larger motors using just fuses and a disconnect. An Overload Relay provides far superior protection, but needs something that it is capable of opening in order to work. An OL relay cannot open a disconnect switch, but it can drop out the electromagnetic coil of a contactor. So the combination of an OL relay and a contactor is called a "starter". Once you have the electromagnetically controllable contactor in the circuit, you can also use it to start and stop the motor through other automatic means, i.e. automation.
A "manual motor starter" still has the overload relay and can disconnect the motor under an overload condition, but it does NOT include the ability to automatically turn a motor on by external means, hence the term "manual". They are also typically limited to small motor controls where the overload disconnect action can be accomplished using springs and such. Above about 50HP, the mechanical forces necessary to keep the contacts from forcing each other apart under normal load make mechanical motor starters difficult to make and use.