I've never had to spec/buy a 'motor starter/protector/whatever the proper name is' before.

I need a recommendation for the least expensive product to protect the motor in the below referenced thread. It would require it's own enclosure. If the enclosure is a separate product, I would appreciate help with that too. Thanks.

http://forums.mikeholt.com/showthread.php?t=186519
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
I've never had to spec/buy a 'motor starter/protector/whatever the proper name is' before.

I need a recommendation for the least expensive product to protect the motor in the below referenced thread. It would require it's own enclosure. If the enclosure is a separate product, I would appreciate help with that too. Thanks.

http://forums.mikeholt.com/showthread.php?t=186519

Use your suppliers. Give them the info you just gave us. That is what they do.

AD is a reasonably priced source for parts but you must assemble them, or I do anyway. This may be more than what you want to attempt. Your suppliers can and will.

A pump panel will usually be the most reasonably priced.
 

kwired

Electron manager
Location
NE Nebraska
There are a lot of options, some maybe not quite compliant if you have an inspector that is particular on details and up to speed on their knowledge of listings, etc.

NEMA contactors/starters will generally be the most expensive, but also will generally have highest number of rated operations for the lifetime of the unit. Definite purpose contactors/starters are likely the least expensive - but technically are only a recognized component and you basically need to be a manufacturer to use them for anything but replacements in a listed assembly - I still see a lot of them being field installed though.

IEC contactors/starters will be considerably less then most NEMA units, usually will be smaller in size and will have less rated number of operations for the lifetime of the unit.

Those rated number of operations seldom mean a lot because field conditions usually cause a failure before the basic number of operations becomes an issue from my experiences.

All of those mentioned are available as open devices (provide your own enclosure), or with a enclosures specifically designed to house the contactor/starter with a variety of enclosure types - NEMA 1, 3, 4, 12, 13, 13x... many also can incorporate disconnecting means and control switches into the enclosure - often known as a combination starter. "pump panel" is basically a combination starter with a fused disconnect, motor contactor and overload, hand/off/auto switch and start pushbutton (for use in the hand mode), and ordinarily is suitable for use as service equipment as well. Pump panels is usually one of the lesser expensive ways to go around these parts - but partly because there is a high volume of them sold here for irrigation applications, this may not be the same for your area.
 

kwired

Electron manager
Location
NE Nebraska
It's on a pool motor type timer. Don't remember amperage rated but I do remember thinking it was sufficient.
I recall the motor being 7.5 hp, seems a little high to directly control that from most timers, some may be rated for 40 amps, but probably only 5 hp. A NEMA contactor will need to be size 2 - you are looking at at least $300-400 for NEMA starter with no enclosure.
 

drktmplr12

Senior Member
Location
South Florida
Occupation
Electrical Engineer
edit time expired!

31 amps might be too high for a manual motor starter, you want to call 1-888-ETN-CARE for Eaton and 1-888-778-2733 for Square D support. The calls should take 10 minutes max. They can tell you better which product to apply.
 

kwired

Electron manager
Location
NE Nebraska
edit time expired!

31 amps might be too high for a manual motor starter, you want to call 1-888-ETN-CARE for Eaton and 1-888-778-2733 for Square D support. The calls should take 10 minutes max. They can tell you better which product to apply.
7.5 Hp single phase is even more restricting then 31 amps.
 