Motor Starter

Status
Not open for further replies.

Kobe85

Member
Location
New York
If I am using a soft starter on a large motor, do I still need to multiply the motors FLA x 1.25 and find a wire that can meet that ampacity?

Isn't the 1.25 multiplier supposed to cover the inrush current? So if I am using a soft starter, wouldn't it seem unnecessary?

Thanks.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
If I am using a soft starter on a large motor, do I still need to multiply the motors FLA x 1.25 and find a wire that can meet that ampacity?

Isn't the 1.25 multiplier supposed to cover the inrush current? So if I am using a soft starter, wouldn't it seem unnecessary?

Thanks.

The 1.25 multiplier has nothing to do with inrush. It covers the service factor.

In any case, the inrush of a motor started across the line is often 6X FLA of a running motor.
 

ADub

Senior Member
Location
Midwest
Occupation
Estimator/Project Manager
The 1.25 sounds like your continuous load multiplier. Service factor is shown on the nameplate and is usually 1.15-1.25. This multiplier is used to determine the thermal overload setting


Sent from my iPhone using Tapatalk
 