motor starter

Status
Not open for further replies.

d1reyad

Member
i been trying to figure how to wire a motor stater correct me if i am wrong but so what i got so far is A! and A2 is the coil a wire from L! to the OL and From the OL back to A! to protect the coil A2 then is control but eiter a switch or a start or stop now what can i use 2 & 3 and the other NC contact for
 
Last edited by a moderator:

buddhakii

Senior Member
Location
Littleton, CO
now what can i use 2 & 3 and the other NC contact for

The skies the limit. Honestly though, first of all your not protecting the coil, you are protecting the motor from starting a fire. What is your coil voltage? If you use a momentary contact pushbutton to start it you will need to use one of the N.O. contacts to create a latching circuit. Search around on the web, I bet you can find some good diagrams.
 

d1reyad

Member
ok i think i got this wrong can someone explain how to wire a 220 motor stater with a start and stop now with a schematic the real contact on a stater like A! A2 2,3 and so on
 

mcclary's electrical

Senior Member
Location
VA
ok i think i got this wrong can someone explain how to wire a 220 motor stater with a start and stop now with a schematic the real contact on a stater like A! A2 2,3 and so on

L 1, 2, & 3 are your incoming line voltage

coil l1 l2 land 120 volt signal (assuming) wire on l1 land your neutral on the NC OL contacts, then back up to l2. This will open the starter if the overloads open.
 
Status
Not open for further replies.
Top