I replaced a motor starter that has been working for about six years. The new one lasted about 1 week. I replaced it again and it lasted about 4 weeks. This is a 9.2 amp 480v motor going to a pump. It is not on a VFD and every time that I test the power it checks out fine. The amperage loads and tempature are also fine.
This is a Size 1 motor starter with a 120 volt coil.
I am with maintenance and I had a electrical contractor check it out this last time and they could not fine the reason that we are frying motor starters.
The power going to the coil reads 125 to 130 volts. Can the power supply to the coil go out and still read 125-130 volts later?
I read 80 to 100 HZ with a Fluke 189, but an enginneer that works here says that I could be getting wrong readings because we have VFD on other motors in the same MCC.
I believe that it is the motor but another person says that they have checked the motor and it is fine. How can I find out if it is the motor?
Do motors cause problems like this?
Could a bad VFD cause problems with a none VFD in the same MCC?
The 20 Amp breaker has not tripped and the heaters have not blown.
Thank You to anyone that can help. This has cost $600.00 in motor starters and $500.00 for the electrical contractor to do what I have already done.
Michael Hester
Electrician
Campus Crusade for Christ
This is a Size 1 motor starter with a 120 volt coil.
I am with maintenance and I had a electrical contractor check it out this last time and they could not fine the reason that we are frying motor starters.
The power going to the coil reads 125 to 130 volts. Can the power supply to the coil go out and still read 125-130 volts later?
I read 80 to 100 HZ with a Fluke 189, but an enginneer that works here says that I could be getting wrong readings because we have VFD on other motors in the same MCC.
I believe that it is the motor but another person says that they have checked the motor and it is fine. How can I find out if it is the motor?
Do motors cause problems like this?
Could a bad VFD cause problems with a none VFD in the same MCC?
The 20 Amp breaker has not tripped and the heaters have not blown.
Thank You to anyone that can help. This has cost $600.00 in motor starters and $500.00 for the electrical contractor to do what I have already done.