This was in a question-and-answer newsletter I received from this site:
-John
I'm amazed by that. The capacity of the service was doubled and it did nothing to reduce the problem. How would you calculate a resolution to that problem? In large buildings, all the office lights don't dim every time an air-handler fires up. What is done differently there than had been done in this case? Is 180 amps the peak instantaneous start-current or does that actually approach infinity?Q7. The lights in my house blink every time my new 5-ton Carrier AC unit starts (180 Amps on start). All conductor terminal connections are secured, so I know that's not the problem. The builder replaced the 6 AWG aluminum to the compressor with 1 AWG, carrier changed the compressor to ensure it was not sticking, the utility replaced the transformer from 25 kVA to 50 kVA, and they changed the service from 2/0 to 4/0 cable. Why do the lights still blink in the house?
A7. The lights blink because the start up inrush current (180A) of new more efficient air-conditioners causes a short-pulse voltage drop on the service conductors. What can be done? Nothing.
-John