motor starting ?

Status
Not open for further replies.

Mike01

Senior Member
Location
MidWest
For motor starting application, with an existing wye-delta starter and 6-lead motor, can the motor be re-connected to delta run and connected to a solid state reduced voltage starter abandoned the wye leads without issues? We have an owner who provided some owner provided equipment the existing starter was wye-delta the new is a solid state reduced voltage?.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
For motor starting application, with an existing wye-delta starter and 6-lead motor, can the motor be re-connected to delta run and connected to a solid state reduced voltage starter abandoned the wye leads without issues? We have an owner who provided some owner provided equipment the existing starter was wye-delta the new is a solid state reduced voltage?.
Well, you CAN just connect it in Delta, in fact you pretty much have to, but that still means using ALL 6 CONDUCTORS, nothing is "abandoned".
 