Hi,
I am trying to properly size a subpanel for motors and pumps and a lighting circuit.
Here's what I have:
15 HP 3 phase
7.5 HP 3 phase
7.5 HP 3 phase
2 120 volt dispensing pumps 20 amps each
1 20 amp lighting circuit (maybe 208 volts)
1 120 volt control circuit
I go to 220.50 Motors
Then 430.24 motors and other loads
This is the 125% of largest motor plus sum of FLA ratings of other motors plus
100% non continuous loads plus
125% continuous loads
I get 191.15 amps
This would be for the minimum ampacity for the conductors.
So I am looking at a 3 phase 200 amp sub panel. Is this correct?
Thanks for your help.
Jeff
Sent from my iPhone using Tapatalk
I am trying to properly size a subpanel for motors and pumps and a lighting circuit.
Here's what I have:
15 HP 3 phase
7.5 HP 3 phase
7.5 HP 3 phase
2 120 volt dispensing pumps 20 amps each
1 20 amp lighting circuit (maybe 208 volts)
1 120 volt control circuit
I go to 220.50 Motors
Then 430.24 motors and other loads
This is the 125% of largest motor plus sum of FLA ratings of other motors plus
100% non continuous loads plus
125% continuous loads
I get 191.15 amps
This would be for the minimum ampacity for the conductors.
So I am looking at a 3 phase 200 amp sub panel. Is this correct?
Thanks for your help.
Jeff