Re: motor taps
Are you installing a motor tap? The rules are in section 430 Part II and 430.28, there are two types of taps, ten feet and 25 feet. Please review the section to make sure we are talking about the same thing, and not a voltage drop issue.
The feeder has to be protected per 430.28. A disconnect is required for each controller per 430.102A)and for a each motor per 430.102(B), with in sight. The motor disconnect has to be capable of being locked open by a permanently installed method, the type of disconnect does not matter, however most often a fusible switch is used.
[ October 28, 2003, 10:46 PM: Message edited by: tom baker ]