Motor Terminator OCP
spectrum
I'm installing a 100HP 480VAC 3PH motor along with its motor terminator. There is a VFD controlling the motor. Do I need to follow the tap rules when installing the terminator at the motor? We're running 1/0 wire to the motor but the terminator only has #10 wire. Can't I just connect the terminator to the motor leads and call it good?
Re: Motor Terminator OCP
I have often wondered about this myself. As best I can tell, the intent of the manufacturer is that the terminator be mounted right on the motor terminals without any fusing. Maybe the terminator manufacturer can give you some insight.
I did some looking years ago and came to the conclusion that the NEC does not specifically cover this device, so that gives you a fair amount of latittude to install it in accordance with the manufacturer's instructions.
Tap rules involve overcurrent protection for the tap. Does the "terminator" have overcurrent protection internal? Does it have installation instructions?
This is a portion of the instructions froma terminator (load impedance matching device) that I have seen before.
If you cannot connect the terminator directly to the motor
mounted junction box, an auxiliary junction box can be
used. However, the terminator-to-motor connection length
should be no more than 6 meters (20 feet).
From http://www.ab.com/manuals/dr/1204/1204-5_0.pdf
Also addditonal info about the product
http://www.abjournal.com/sept2001/departments/tech_tips/riding_out.html