Our local utility provided a product which came up short. One of three phases was missing. Well I lost a few motors, (poor OL selection), but thats not what my questions about... I have never tested a submerged motor such a well pump with a megger, I followed normal motor testing procedures and the motor megged bad, ( ground on each phase), I confirmed findings with 2 meggers, (Fluke, and real Megger). I also noted that the OL didn't trip, so I don't know if this motor was running at the time. The motor was run tested, (against my judgement), and ran... I was surprised CB didn't trip, yet I treat every day as a learning experience, and desire to learn why this motor submerged in water failed the megger check. I am guessing that submerged in water has quite a bit to to with it but desire any comments, help or suggestions to provide a better testing procedure as I have 4 well pumps total and will surly test one of them again...
 

stickelec

Senior Member
Since your pump was still in the well maybe the cable was the culprit not the motor. What was your meggar reading?

I assume the pump was still in the well for the run test, how did the current look?

You cannot reliably depend on your OL to protect against single-phasing.
 